Lovecrusher posted:So, my question is, should I take the fact that this tailpeice is so hard to find as an indicator that I'm heading towards a world of hurt and clogged drains? Is plumbing the drain into the bathroom ill advisable? The sewage mainline is close so I could alternately plumb into there, but I'm not too excited to have the possibility of a clog blowing poo poo back up to the dishwasher and all over my dishes.
|
# ¿ May 22, 2009 18:31 |
|
|
# ¿ Apr 27, 2024 01:09 |
|
benitocereno posted:I don't know anything about the freezing point with PEX, do they make insulated tubing if that's an issue? PEX really is great stuff; I think it gets a bad rap just because it's so simple, so cheap and so reliable that anybody can do it. It's almost too easy... It's lead to entirely new approaches to plumbing- PEX houses often don't have networks like copper houses do, but instead use a manifold near the water heater with runs directly from there to each fixture. (It's about the same price to run 5 individual unbroken 1/2" lines to a bathroom than it is to run 3/4" hot/cold and split them out in the walls.) The worst part was that it required a $100+ crimp tool to crimp the copper sleeves onto the fittings (and you need 3 different sizes...), but new fittings now have made it less of an issue for small DIY jobs. Those shark-bite fittings are pricey, but they're great if you don't have access to a crimp tool, or if the space is simply too tight to use a crimp tool, like it often is under sinks. grover fucked around with this message at 18:56 on May 26, 2009 |
# ¿ May 26, 2009 18:42 |
|
Rd Rash 1000cc posted:The problem with insulating a cold line in a cold space.Is you're more likely to keep the heat out instead of keep it in. This is why i'd suggest insulation the joist and not the pipe itself. grover fucked around with this message at 18:57 on May 26, 2009 |
# ¿ May 26, 2009 18:50 |
|
I think he meant the water supply, not the DWV.ZentraediElite posted:The upstairs toilet in my dad's house whines/whistles when you flush it. Is this something to worry about? About 15 years ago the toilet broke in the night and did a bunch of damage to the floor/ceiling of the room below it. I'd hate for this to happen again.
|
# ¿ May 26, 2009 22:10 |
|
Antifreeze? Heh, don't they just, you know, drain the water out so it can't freeze? Not rocket science. Just run the water until it stops burping air bubbles.
|
# ¿ May 28, 2009 03:41 |
|
Have you tried PB Blaster or WD40?Lucid Smog posted:Also, does the same prime and then cement rule apply to drain lines? I'm going to be adding an auger access to some 1.5" drain pipe in my basement soon. As to the yellow one-step cement... it's for CPVC only, and whether or not it's legal depends on the local code. I don't see anything in IBC that would prohibit it. If local codes specifically require a pre-application of primer, it may be a "letter of the law" thing.
|
# ¿ May 28, 2009 14:30 |
|
Rd Rash 1000cc posted:
|
# ¿ Jun 12, 2009 02:28 |
|
Rd Rash 1000cc posted:No it's not. Show me the code where it says its legal. Its connected and since its so far down near the trap if the sewer backs up it will most likely back up into the dish washer. Oh, the code that says this is legal is IRC P2717.3, btw. Says so quite explicitly. The hose should be supported so that some part of is is fastened to the bottom of the counter is the only thing not quite right; otherwise, the line can fill up with crap from the sink and clog. grover fucked around with this message at 03:09 on Jun 12, 2009 |
# ¿ Jun 12, 2009 02:56 |
|
Rd Rash 1000cc posted:I follow the UPC. The Air gap will help prevent if the sewer backs up from going into the dish washer because one its a the rim of the sink (highest part of the ficture). Just because you're not in a flood level doesn't mean a sewer cant back up. If someone flushes something stupid and it clogs a drain line, it could back up into the lowest fixture. Now usually that's the shower would be the lowest but if the kitchen sink is for some reason it will back up there. It will go into your DW and gently caress it up. Please quote UPC, I'm interested in what it says; I have a feeling you're reading it wrong and then IPC/IRC and UPC are saying the same thing in slightly different ways. (Ignore the highlighting, that was from another project I did a couple years ago.) My copy of IPC 09 is at work; I only have IRC 06 handy right now. grover fucked around with this message at 03:25 on Jun 12, 2009 |
# ¿ Jun 12, 2009 03:18 |
|
OK, I apologize, UPC does require it. IPC and IRC, however, do not. I've never seen an air gap on the drain line of a dishwasher, but I've always lived in IBC states- all they do is loop it up under the counter. Who uses UPC as opposed to IBC? I thought US was 100% IBC now.
|
# ¿ Jun 12, 2009 13:05 |
|
dyne posted:QUESTION: How do I replace a shut off valve (or plug up the pipe) under the kitchen sink when there's still a small amount of water flowing through it? A temporary fix would be fine just so I can turn the hot water back on and shower
|
# ¿ Jul 20, 2009 00:10 |
|
dyne posted:
|
# ¿ Jul 20, 2009 10:51 |
|
dyne posted:After the meter, the pipe is wrapped in plastic over some sort of thin insulation, just by squeezing it I can't feel anything other than pipe.
|
# ¿ Jul 21, 2009 10:46 |
|
Audio Rules posted:Hello plumbing wizzards out there. We are having a recurring problem with a clogged trap in the bathroom sink. I've found these alternative no-clog traps that promise to solve the problem. Hmmm... Of course, I don't really need to ever stop up the sink, maybe I aught to just remove it completely.
|
# ¿ Jul 28, 2009 23:13 |
|
Rd Rash 1000cc posted:6 months isnt bad. I would suggest stop washing hair down the drain, and honestly how much tooth paste do you brush with that makes it so think it clogs poo poo.
|
# ¿ Jul 29, 2009 02:59 |
|
Saltin posted:That's just it, I am having an issue. From time to time, when I open the dishwaser, I notice it is full of water. This water isnt water left over from the dishwasher not draining properly. It isnt water from a leaking water supply. kid sinister posted:Are you on the bottom floor? It sounds like you have a clog in the drain stack for your column of apartments in your building and the poo poo flowing out of your sink is from the apartment above. Capping it would only cause the stack to fill up and eventually cause the same problem in your upstairs neighbor's apartment, possibly leaking down into your kitchen, again... grover fucked around with this message at 22:46 on Aug 24, 2009 |
# ¿ Aug 24, 2009 22:42 |
|
Red PEX is supposed to be for hot water, and blue for cold, that's why they make it in different colors! Now you've gone and confused everyone :P I found my wife's garden shears to cut PEX even better than expensive special-made cutters.
|
# ¿ Sep 2, 2009 01:26 |
|
Rd Rash 1000cc posted:Oops i had my pex backwards on the A and C.
|
# ¿ Sep 5, 2009 14:02 |
|
TraderStav posted:What other information can I provide? 2) Where is the smell coming from, and is the P-trap the smell is coming from getting siphoned dry after you do a load of laundry?
|
# ¿ Sep 28, 2009 00:06 |
|
The p-trap is an ingenious invention that uses a small bit of standing water to block the sewer stink from seeping out every sink and drain in your house. The ones in your sink are easy to see, but floor drains, showers, etc, all use them too. They work in tandem with vent pipes and stacks- if a vent is clogged and you dump a lot of water in the pipe at once (like when a washer drains), the p-traps can get siphoned out, and the stink will escape. I suspect this is what's happening to you. If you can verify, we can try to help point you in the right direction
|
# ¿ Sep 28, 2009 00:12 |
|
Drain line must slope down, vent line must slope up. One line can *maybe* be both if it's short enough, otherwise you'll need separate drain and vent pipes. Hot and cold water lines are fine regardless of routing. It's legal to have them running exposed outside your wall/behind your dishwasher, but not aesthetically very nice. You may run into issues with the size of the pipes of the inspector does the math (you can only put so many sinks/appliances on a single drain line or water supply) but they probably won't care if you do everything else right.
grover fucked around with this message at 00:42 on Oct 29, 2009 |
# ¿ Oct 28, 2009 10:50 |
|
Whattup, Pappy?Rd Rash 1000cc posted:I should have graded those lines correctly in my drawing. Speaking of which, found the table I was looking for. (IRC P3105.1) At 1/4" per foot slope, you can have 5' of horizontal 1.25" pipe between the bar sink's p-trap and the drain/vent connection. If using 1.5" pipe, it can go 6'. grover fucked around with this message at 00:53 on Oct 29, 2009 |
# ¿ Oct 29, 2009 00:51 |
|
Rd Rash 1000cc posted:whats the smallest pipe you use to vent a single fixture?
|
# ¿ Oct 30, 2009 00:55 |
|
Yeah, that's BS. I'm not going to say it's not done, but it's certainly illegal in all 50 states and there seems to be 0 reason to do it that way.
|
# ¿ Oct 30, 2009 02:22 |
|
Rd Rash 1000cc posted:I'm not sure if you already posted it but what type of plumbing do you do grover? Are you commerical, resi, or service. And union or non union? grover fucked around with this message at 02:59 on Oct 30, 2009 |
# ¿ Oct 30, 2009 02:57 |
|
As a stop-gap, you could adjust the temp of your water heater hotter. Just be mindful of scalding! Less hot water for a given temp shower will stretch the tank a little longer. You can also get valves that go on your shower head to reduce the flow. I did both of these until we upsized our tank, and it can really help. Even a relative trickle makes for a nice long comfortable shower. Edit: Scald temperature chart showing the number of seconds it takes to get a 2nd degree burn at different water temperatures (EG, don't ever set it above 135F, and even that's getting pretty dangerous, especially for kids): grover fucked around with this message at 02:35 on Nov 21, 2009 |
# ¿ Nov 20, 2009 20:15 |
|
100 HOGS AGREE posted:So the chrome piece coming out of the wall, does that just screw in back there and will I be able to put it back later?
|
# ¿ Dec 13, 2009 20:37 |
|
How long does your hot water last, though? Most of those tanks only allow for 15-20 minutes at the most, and two heads will probably cut that about in half.
|
# ¿ Dec 20, 2009 20:18 |
|
"[panic posted:"] There are a couple causes; one is if a sink/whatever isn't used often enough, the water can evaporate. This is easy to fix- just pour some water into it every once in a while. Another cause is clogged vent lines. If vent lines clog, the P-trap can be siphoned dry. Symptom of this are bubbling whenever you use a lot of water (there should never be any bubbles coming back up), or the toilet draining almost completely dry after flushing. In this case, you've got to snake the vents to clear the clog.
|
# ¿ Jan 18, 2010 15:01 |
|
slap me silly posted:Hah, just what I need to hear now that we've established I have a cast iron sewer pipe and it's loving freezing in these parts. Methylethylaldehyde posted:gently caress freezing ground. The cast iron sewer pipe loving up and broke under the house because of freeze/thaw pressures. I just paid $180 to get the fucker snaked out after a tidal wave of poo poo colored water flooded into my garage after taking a shower and doing a load of wash. Regardless, $15k seems ridiculous. Digging up and patching concrete isn't nearly that expensive! The real problem is finding exactly where the pipe is leaking; someone with the right equipment should be able to find it pretty easily, though. I don't see this costing more than 2 grand, tops. Probably cheaper than that. grover fucked around with this message at 18:07 on Feb 12, 2010 |
# ¿ Feb 12, 2010 18:03 |
|
Methylethylaldehyde posted:Gotta dig a trench to the street 8-12 feet down. That's a big loving backhoe, and a huge metric fuckload of dirt that needs a place to go. Also, most certainly NOT freezing if it's that deep.
|
# ¿ Feb 13, 2010 06:17 |
|
Methylethylaldehyde posted:Alaska, pipes have to be down that far when they leave the house, otherwise you end up with pipes that break because of the temperature differential between the frozen ground outside and the warmer soil under your house. As per the plumber who just did one last week, they're usually 8-12 feet down depending on the house's location and what kind of soil is present.
|
# ¿ Feb 13, 2010 06:26 |
|
dwoloz posted:I'm in contract to buy a 1920 San Francisco Bay Area home with copper plumbing Or, you can just pay for the general home inspection and see how comfortable you are with his/her report and go from there. If they indicate problems in certain areas, you can have a pro come in and look at them closer, give price quotes, etc.
|
# ¿ Feb 15, 2010 18:15 |
|
mr.belowaverage posted:For what it's worth, my home inspector was a P.Eng and didn't spot the following, in one bathroom alone:
|
# ¿ Feb 18, 2010 23:23 |
|
That sounds very likely- no other reason you'd put in a mixing valve in this situation, especially considering the size of your tank and cost of the mixing valve. Tanks lose surprisingly little energy through the insulation, so unless you need to heat the water overnight with cheap electricity, you might as well remove the valve and eliminate that point of failure. You can go hotter than 120F, but I wouldn't go above 135F, the scalding risk is too high. You can always test and adjust to your liking, too. grover fucked around with this message at 19:05 on Feb 28, 2010 |
# ¿ Feb 28, 2010 19:02 |
|
Rd Rash 1000cc posted:Dietcokefiend i suggest opening a window when you are around the glue next time. Is it the same way with plumbing?
|
# ¿ Mar 21, 2010 11:44 |
|
Hank Killinger posted:Toilet plumbing question: This weekend, I heard drain burping coming from my apartment bathroom so I went in to see what was up. The burping had stopped before I reached the bathroom, however I heard a faint fizzing noise; so I played a little game of find the sound. I eventually pinpointed the sound to a panel on the base of the toilet bowl which covers a bolt (that I assume holds the toilet to the floor). White bubbles, which looked kind of like soap suds, were enveloping the panel. grover fucked around with this message at 14:10 on Mar 23, 2010 |
# ¿ Mar 23, 2010 14:07 |
|
Papercut posted:What should I do? This is the only toilet in the house, and I'd like to go to the bathroom again today.
|
# ¿ Apr 3, 2010 23:23 |
|
Beer4TheBeerGod posted:Here's a good article: http://www.energysavers.gov/your_home/water_heating/index.cfm/mytopic=13040
|
# ¿ Apr 4, 2010 01:26 |
|
|
# ¿ Apr 27, 2024 01:09 |
|
Beer4TheBeerGod posted:It's a passive system, basically one pipe wrapped around another. The drain water is always hotter than the incoming water. One example, the GFX exchanger, retails for around $500 or so. Here's what they look like: So, I guess a better example would be when your dishwasher is draining... er... nevermind. It *would* work when you're taking a shower, though! That design looks horribly inefficient, though. Water falling through there will spend so little time, virtually no heat will be transferred. I can guarantee you spend more money (and energy) making/installing that than you'll get in a lifetime of showers. Not to mention you'd have to separately plumb your gray water and toilets, which costs more money/energy, too. As in most plumbing "free energy!" schemes, you're better off just taking shorter showers. If you really want to save energy, put a "Navy shower" fast cut-off valve on your shower head. And yeah, you might actually see energy pack back on your $2 valve investment and 5 minutes it would take to install grover fucked around with this message at 19:54 on Apr 4, 2010 |
# ¿ Apr 4, 2010 16:48 |